jeepnjeff

New Member
Question:
If a 10 :1 transformer has a 120v at 1 amp on primary, what would you read on secondary Volt? AMPS?

Is the primary the larger and the secondary the smaller?

Im not sure how to go at this problem. Clues please!
 
The primary or secondary is only a matter of viewpoint. Apply AC to the 10 turn ratio side and you'll get 1/10th out the other, apply ac to the 1 turn ratio side you'll get 10 times out the other, the primary is which side is driven by power. Obviously with wire thickness to consider there are power consideration in what you can safely step up and down.

No load voltage is one way of measuring it, but commonly with a transformer the 'voltage' it's rated at is at a it's rated current. No load voltage will always be higher.
 
Last edited:
The Volts * Amps should be the same on the primary and the secondary. So 120*1 =12*0.1 is wrong.

Mike.
 
Voltage goes down with a 10-1 transformer, but current goes UP. It depends on the wiring and the core to exactly what you're going to get out.
 
Yes that can be a little confusing. The voltage ratio and current ratio work in reverse, so if you step up the voltage by 10 you decrease the current by ten, and if you step down the voltage by 10 you increase the current by ten. For learning purposes just assume the transformer is a 'perfect' device so power into the primary will equal power out the secondary. In real life there are some losses as nothing is 100% efficient.

Lefty
 
The voltage loss in the primary/secondary is easily calculated by measuring their non-connected DC resistance.
 