So here is a description of the entire system just to help clarify. In the images of the whole system, the very, very fine thermocouple wires extend out of the center of the heating pad. There are also a set of black/red and black/yellow wires that run from the edges of the plates out of the box and into the dimmers (to be honest, I'm not sure what the dimmers are for). From my understanding, the thermocouple is not what is controlling the temperatures, but rather what is measuring it. Is that correct?
That would leave me to believe that the larger wires connected to the dimmer would control the power being supplied to the plates.
Also, if someone could explain what the function of the controller and the relay are in general that would be helpful. I literally do not know much of anything about electronics so if you could spell it out in laymen's terms as best as possible that would be helpful. Abbreviations and acronyms are hard for me to understand aside from AC and DC. We actually do have a DC power converter that plugs directly into the wall socket which makes me wonder if we even need the relay module at all. To me it sounds like the relay is just to drop the voltage from anywhere up to 250 volts back down to twelve. Is there a way I can just plug the DC power supply directly into the controller without the need for the relay?
The DC power converter wall plug has two wires, one brown and one white, but I'm not sure which wire is positive and which is negative.
If I do still need the relay module, then I can still use the diagram showing the thermocouple leads going into the controller. That part makes sense to me. What kind of wire runs from the open collector outputs to the relay though? I don't think I have those wires.
The temperature range that we are trying to achieve is anywhere from 0 to 40 degrees celsius. Are these temperatures too low for the PID controller.
My take on what you have is this. The large wires on the heating pads are power to the pads. Yes, they run directly to the dimmers. The thermocouples actually just measure temperature. The thermocouple itself does not "control" anything, it merely provides a signal proportional to the temperature in the heating pad center. I believe they were to allow you to monitor temperature. Enter the dimmers. The dimmers were used to provide an adjustable voltage to the heater pads. The lower the voltage to the pad, the less current the pad will draw and the less heat it will produce. Therefore, if you only read the temperature using the thermocouple, you could adjust the dimmers to hopefully maintain the desired temperature at the heating pads. This involves sort of finding a "sweet spot" on the dimmer. This is really not control. The Omega controller you have could be used to simply monitor the temperature of the pads. Then the dimmers slowly increased and allowed to settle searching for the sweet spot. This amounts to placing a pan of water on a gas stove and slowly increasing the flame to maintain the water at a specific temperature. As long as room temperature doesn't change and not too much water evaporates (the water is the load) we can hope to maintain the temperature fairly well.
The drawing I provided actually uses the Omega controller to control the temperature based on the temperature received from the thermocouple. This is where the method used with the controller for control can get a little complicated. The simplest method is what they call On / Off control. The controller has a set point, that being your desired temperature. When the process variable (the temperature of the pad) is below your set point the controller closes a relay and applies voltage to the pad. When the process variable meets or exceeds the set point, power is removed. The On / Off cycle repeats. The load (your petri dish) will hover above and below set point. There are many factors that will determine how high and how low (deviations from set point) you will have.
Your controller also offers what is called PID (Proportional Integral Derivative) control. This is a complex process but in real simple terms the controller looks at the process variable and the set point. As the difference between PV and SP closes the controller will for one example begin to pulse the relay providing power to the heater. This prevents a large overshoot in temperature and the process should maintain a much better control maintaining SP (Set Point).
Now you mention a temperature range of 0 to 40C (32 to 104F) if you have heater pads and no way to make cold then there is a problem as you can never get a temperature below ambient room temperature.
Back to the heating pads. I have assumed they were simply heating pads. Another member made a good point. There are devices called peltier pads that can make hot and cold. I have based everything on heating elements or heating pads.
Ron