center tap transformer current rating

Status
Not open for further replies.

wakoko79

New Member
[solved] center tap transformer current rating

if the transformer has a rating of 3A, does it mean the maximum safe current draw from center to right is 3A? What if I'm not using the center and instead, I'm using left and right terminals (using fullwave)? Is the maximum still 3A? thanks
 
Last edited:
The 3A is the current rating though the winding, either from end to end or end to center-tap. But that's an RMS rating and is more than the DC filtered current you can draw from a rectifier connected to the transformer. That is due to the high peak currents that a rectifier and filter draw, which causes the RMS current level to be above the DC current level.
 