Motor Reversing Intermittent Duty DPDT Solenoid Relay

Status
Not open for further replies.

I need to have a conversation with whoever wrote the test spec; they obviously put no thought into this at all, or they don't have a clue about what they are doing!!!!

First, what does 1.5sec Off mean??? No fan motor I have ever seen will begin to coast to a stop in anything like 1.5sec, so in-effect, you are trying to reverse the motor while it is still spun up in the previous rotation.

This causes the motor to draw huge transient start-up currents, likely 3X what it would be if you were starting the motor from a stopped condition. This is an extremely unnatural thing to do to the motor, and likely never happens in an automotive application. In fact, I have never seen a fan motor in a car that turns both directions. I'm guessing that it would take the motor up to 20sec to coast to a stop if it had just the aerodynamic braking of the fan.

So, is this what is really intended?

Second, if the goal is to actually reverse the motor so quickly, then using dynamic braking by shorting the motor (or connecting it to a braking resistor) will stop it faster than just letting it coast to a stop under the influence of aerodynamic braking caused by air against the blades.
That should have been specified as part of the test.

So what are you trying to do to the poor motor???
 

I am trying to kill the motor, in short looking at its life span.
 
Yes. Look at the Green trace in this image:



That is the voltage applied to the motor terminals.

Mike,

I am going to run 8 fans at a time. Each fan draws about 7-8amps. Do you think I can still run the test set up with all the fans? Would there be any damage to the diode (1N4001)?
 
Mike,

I am going to run 8 fans at a time. Each fan draws about 7-8amps. Do you think I can still run the test set up with all the fans? Would there be any damage to the diode (1N4001)?

Since the motor current doesn't go through any of the diodes, no.

The two motor relays (U4 and U5)will have to be large contactors like the ones Kinarfi showed in his pictures. Look for regular 12Vdc Contactors;not Starter Relays.
 
Since the motor current doesn't go through any of the diodes, no.

The two motor relays (U4 and U5)will have to be large contactors like the ones Kinarfi showed in his pictures. Look for regular 12Vdc Contactors;not Starter Relays.

Thanks. I will look into it.
 
I check my solenoid, won't work, gets hot.
https://www.digikey.com/product-sea...=0&page=1&quantity=0&ptm=0&fid=0&pageSize=500
check these out, 70 Amp 12 v 125 ma coil
You are going to need 4 of them because they don't have SPDT, just SPST.
I added a drawing based on Mike's Toggle1.asc and put diodes across all coils + a bridge diode set on the fan, it may be advisable that each fan have a set of bridge on it's terminal, Mike Please Comment.
Kinarfi
 

Attachments

  • Toggle1k.asc
    7 KB · Views: 162
Last edited:
Starter relays or solenoids here in the uk are not meant for continuous operation, you might burn out the coil.

Might be worth talking to a mobile plant service centre or a motability centre, large 100s or more amp contactors are used in mobile handling equipment, not so much these days due to igbt's and fets but they are still around.

If having 2 relays or more on accidently would cause a short then electrically interlock the relays coils using spare contacts making it impossible.
 
Last edited:

dr pepper,
Thanks for the information. It's been tough working on this.
 

Kinarfi,
Right now I'm working on Mike's circuit. I'm going to test it with 1 fan & see if it works. It works in the software. I'll update once I test run the 1st fan.
Thanks.
 
Since the motor current doesn't go through any of the diodes, no.

The two motor relays (U4 and U5)will have to be large contactors like the ones Kinarfi showed in his pictures. Look for regular 12Vdc Contactors;not Starter Relays.

Mike,
I have the test set up per the circuit diagram. The fan runs in only one direction though.
Secondly are the diodes arranged correctly (I mean the current flow direction)?
Thanks.
 
Last edited:
I started late on in the threads, is the schematic a relay flip flop?

The 2 relays with 6v coils might be the issue.

I've used a 2 relay flip flop circuit a couple of times on some old equipment we have.
 
I started late on in the threads, is the schematic a relay flip flop?

The 2 relays with 6v coils might be the issue.

I've used a 2 relay flip flop circuit a couple of times on some old equipment we have.


I believe so. Does it contradict your flip flop circuit?
 
Nope there are many ways of doing it, the number of relays in your circuit is probably the minimum you need.
 
Have a look at this:

https://www.emil.matei.ro/onof2.php


I think your issue is possibly a mistaken connection, however if you read the blurb you can see that this and your design rely on one thing about the relay, that the holding current is much less than the pull in current, I suspect that if there are no errors with your circuit this might be along the lines of why it isnt working (not wanting to poop on anyone), the design of the relay plays an important part.
Double and triple check your connections before you condemn your circuit, might be worth building just the push on/push off circuit and see if that works on its own.
 

That is the reference I linked to way back in post 15 of this thread.

That is also the basis of the toggle part of the .asc files I posted earlier. It simulates just fine with relays that have a hold-in current of ~1/3 of its pull-in current.
 
I built the flip flop earlier to day and it worked just dandy, definitely going in my neat diagrams folder.
Kinarfi
 