I would expect the LED to stay on the whole time that the relay is on, and so I would not expect it to blink. I understand "blink" to mean turn on and off repeatedly, like a vehicle turn signal, or to turn on once for a very short time.the LED is also blinking when relay is turning on.
Dear MikeThere is a switch output and an analog output. Which are you using. The analog is rated 20ma (current loop) and the switch output is rated maximum 125ma. However, the pressure unit uses up to 40ma itself without load.
The relay will only take 22ma, so no resistor is necessary if the output can supply 22ma or more.
You don't specify which pins are which in your diagram, so one can only guess what output you are using. Guessing will not give you a proper answer...
Maybe post what the pressure units actually are, and what the pinouts are.
Thanks for your quick and elaborated reply. I’ve checked all the points that are mentioned in the response . Power terminals of the relay are correctly connected (not represented correctly in circuit which is a mistake and has been rectified) and the LED is also blinking when relay is turning on. Trying to arrange some more details but in the meantime would it be advisable to use a resistor in between relay and PS-1 to control the excessive current (revised circuit attached).It appears that the first pressure switch powers the second pressure switch, which in turn power the relay.
The G2R-2-SND relay contains a diode to reduce the inductive voltage spike when the relay is turned off. The diode is fitted so that pin 8 is the positive connection, and pin 1 is the negative (https://assets.omron.eu/downloads/d...-s_(s)_general-purpose_relay_datasheet_en.pdf on page 9)
Your circuit shows the relay coil being the wrong way round. The diode will short out the output of the pressure switches. I don't know why the circuit is working at all, but there could be something in the relay that limits the current in the diode.
You should check the polarity of the relay coil. Pin 8 should be at 24 V when the relay is on. Also you should measure the current in the wire from the second pressure switch to the relay coil. It should be around 22 mA when the circuit is on.
The relay contains an LED indicator. If that is not turning on when the relay operates, would indicate the relay coil is powered the wrong way round. However, it's possible that the indicator will work either way round. It's also possible that the relay is arranged so that it doesn't matter at all which way round it's fitted, but it's always best practice to connect as shown in the data sheet.
Also the pressure switch is rated up to 24 V +/-10%, with 10% maximum ripple. That give a maximum peak voltage of 27.6 V. I don't know what power supply you are using but many supplies rated at 24 V could exceed that at times.
The load is connected to the same supply. When the load is turned off, there will be a voltage surge, temporarily increasing the supply voltage. Without more details, it's not possible to work out how big that surge would be. In many circumstances it would be too small to measure, but in some circuits it would be significant. As you are already close to the maximum voltage that the pressure switches can handle, that could be a problem. It depends on the size of the load, the characteristics of the the power supply, other loads on the power supply and the characteristics of the wiring joining it all together.
Dear Mike,Your pressure switched seem to have a max current output of 20mA and your relay requires 22mA. Looks like something needs to change. Do you know how to use a transistor to switch your relay?
Mike.
Dear SagorThere is a switch output and an analog output. Which are you using. The analog is rated 20ma (current loop) and the switch output is rated maximum 125ma. However, the pressure unit uses up to 40ma itself without load.
The relay will only take 22ma, so no resistor is necessary if the output can supply 22ma or more.
You don't specify which pins are which in your diagram, so one can only guess what output you are using. Guessing will not give you a proper answer...
Maybe post what the pressure units actually are, and what the pinouts are.
This schematic does not show the coil inductance which stores current (and energy) and the coil resistance that limits current nor the flyback diodes needed to suppress over-voltage (V=LdI/dt) on the pressure switches. This is a simple problem that might be easily fixed if your schematic was more logical and accurate with these parameters.
Coil Type: | Non-Latching |
I am uncertain why/when the PNP transistor switch fails in the pressure switch. But if any inductive DC current is interrupted or switched off fast, there must be a snubber or clamp diode to absorb the flyback voltage. The relay coil is supposed to have one flyback diode built-in, but the solenoid coil does not.
The relay contacts are rated for 3A inductive but that would reduce MTBF significantly to << 1% and also create large kV voltage spike that might short out PS-1 PNP switch by wire close proximity inductive crosstalk. Better wiring might be twisted pair, STP (shielded twisted pair) cable and routing at 90 degree to reduce potential crosstalk