i can reduce it to 200 A. do you hv any idea how to do that250A @ 50V is 12.5kW.
If the 3-phase power is 240V, you could draw 13.3kW @ 32A.
So with a very efficient switching power supply (likely custom) you should be able to get the output you want.
But that's certainly not a trivial design.
Hello everyone
What are the possible options of getting 250amps 25-50Volt dc power supply. My lab has access to 3 phase supply but maximum current rating is only 32 Amps.
220 volt per phase3ph supply: 32 amp rating at what voltage??
Do you need it regulated or not?
Max.
and I need voltage regulation3ph supply: 32 amp rating at what voltage??
Do you need it regulated or not?
Max.
Can you send me some links of manufacturers. I tried viquor but they dont have itAt that power level I would not try to build my own unless you are knowledgeable about high power supply design.
You should buy a commercial device, but they won't be cheap.
Atleast one two hour per dayFor how long do you need 200 Amperes at 50 Volts ? Is it a few minutes operation or permanent draw supply ?
Where did you get 0.7kva?0.7Kva is no where near 12.5Kva power required.
Max
.
I can not afford that supply. Probably no one makes it.i can reduce it to 200 A. do you hv any idea how to do that
What are the precaution I need to to take.I can not afford that supply. Probably no one makes it.
Look for two 100A supplies, or four 50A supplies. ( I have on of those)
You can parallel supplies. Not the best but we do it all the time.
If you are going to parallel supplies:What are the precaution I need to to take.
For 3-phase 240V, 32A the power is √3 * 240 * 32 = 13.2kW.OK 7kva but still now where near 12kva!
Max.
Atleast one two hour per day