CBB, you are correct. This is how it is working. I need it to work opposite.) Robot triggers chuck close signal to solenoid. (The trigger is not a 24V signal, but removal of the 24V signal. The 24V signal is applied to the valve in it's normal state(chuck open.) I want it to be applied when I select chuck closed.
Thank you all. It appears that I can use the same valve, just use an Off-Delay Timer function as Strantor suggests. It was also suggested by a former college to use a Smart Relay. ("That whole setup kind of sucks because the Star is reverse logic, meaning 0 volts is on, 24 volts is off. On the relay side if the logic states are a problem, get a smart relay from Newark. You can learn to program that in 5 minutes and set the timer and logic up anyway you want.")
I think either one of these I have here would work. Would you agree?
http://www.automationdirect.com/adc...l_Counter_-z-_Timer_-z-_Tachometer/CTT-1C-D24
http://www.newark.com/idec/fl1e-h12snd/smart-relay/dp/50R9725