These are general voltage ranges for six-cell lead-acid batteries:
Open-circuit (quiescent) at full charge: 12.6 V to 12.8 V (2.10-2.13V per cell)
Open-circuit at full discharge: 11.8 V to 12.0 V
Loaded at full discharge: 10.5 V.
Continuous-preservation (float) charging: 13.4 V for gelled electrolyte; 13.5 V for AGM (absorbed glass mat) and 13.8 V for flooded cells
1.All voltages are at 20 °C (68 °F), and must be adjusted -0.022V/°C for temperature changes.
2.Float voltage recommendations vary, according to the manufacturer's recommendation.
3.Precise float voltage (±0.05 V) is critical to longevity; insufficient voltage (causes sulfation) which is almost as detrimental as excessive voltage (causing corrosion and electrolyte loss)
Typical (daily) charging: 14.2 V to 14.5 V (depending on manufacturer's recommendation)
Equalization charging (for flooded lead acids): 15 V for no more than 2 hours. Battery temperature must be monitored.
Gassing threshold: 14.4 V
After full charge, terminal voltage drops quickly to 13.2 V and then slowly to 12.6 V.