I think he is blowing smoke, as long as you do not exceed roughly 1Kva in operation then there should be no problem.
What load do you plan on using?
Max.
What load do you plan on using?
Max.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
"About up winding of Toroidal that is 19 Volt to 27 Volt. Its not technically possible. Coz your existing power rating changes from 1000 VA. To 1500 VA.
If we do this then your primary winding will be damaged."
Can someone please confirm if this claim is indeed true?
This will leave the power rating at 1000VA.If you increase the voltage per winding from 19 to 27v, the current rating will reduce to 26 x (19/27) = 18 Amps.