What sort of AC motor is this?
Three phase?
If so then all the coils should have the same impedance.
Remove the rotor (so there's no loading) and test each coil individually by connecting it up to the output of a 24VAC transformer. Measure the current through each coil separately, you should get similar readings from each coil, if one's out by more than about 5% then I would consider re-winding it or replacing it if re-winding isn't an economically viable solution.