If 3000 amps of current is being pulled from a distribution line, then the distribution line HAS to be carrying 3k amps, does it not?
Do you know the distribution line is probably running something like 15 kV to 20 kV through the residential area lines? At each "drop" the transformer steps it down to 220V to feed each house so there is a current reduction of about 100X at each transformer going up to the high voltage side.I have read that power lines carry high volts to reduce power losses and that a single distribution line might only be carrying 30 of 40 amps. I dont understand this bc that line may be feeding dozens of homes, each of which might be using 30 amps at a given time. Someone tried to explain to me that it had to do with the transformer and shifting the voltages to a lower level to keep the power level. I understand that say wattage is the same for 120v 3a and 12v 30a. What I dont understand is why the distribution line can feed 100 homes at say 30 amps draw each and not be carrying 3000 amps.
Also, same thing on an ac to dc power supply. Lets say I have a 20a breaker and I want to plug in a bunch of computer power supplies that are 12v 10a. Could I plug in 2 or 10 before I tripped the breaker (assuming I was pulling a full 10a DC from each).
Thanks.
It has nothing to do with AC or DC, both work identically - the reason AC is used is because it's easy to convert the voltage (and current) using simple transformers.
Some times it is hard to know what is on a single breaker. Many people wire the lights in the same breaker as the plugs. I hate this I like the light on a different breaker. Some times two or three rooms are all wired together.15 amp breaker where you are running multiple stepper motors, a heated print surface, and a heat block for extrusion.
Yep. We used to make a 1kW bench supply that ran on 110VAC. Using unity power factor (and 100% efficiency) you would think the AC line current would be about 9A. But the power factor for a diode/cap bridge offline running off single phase power was about 0.58 ballpark and the converter efficiency was actually about 85% so the actual RMS AC line current was more like 18A which meant you had to have a 20A service (breaker) to run it.Ac adds all sorts of weirdness. The NEC (National Electric Code) in the US also adds some.
The NEC would size a circuit based on loaded 80% continuously. Continuous has a definition too.
AC and motors makes thing weird too. Something called power factor.
Yep. We used to make a 1kW bench supply that ran on 110VAC. Using unity power factor (and 100% efficiency) you would think the AC line current would be about 9A. But the power factor for a diode/cap bridge offline running off single phase power was about 0.58 ballpark and the converter efficiency was actually about 85% so the actual RMS AC line current was more like 18A which meant you had to have a 20A service (breaker) to run it.
Lots of good info there. Thanks!
Just add my 2 cents worth of facts as I work in the electrical distribution industry.
No, that is the RMS line current that the unit draws because of PF. A single phase unit running diode bridge and cap input has a power factor under 0.6. Add efficiency losses and your AC line current is about double what you calculate based on "ideal" with unity power factor. It's not surge current it's continuous.Are you sure it wasn't just the surge current taking out a smaller breaker? - it's a VERY common occurrence if you have a lot of TV's, like in a TV shop, and of course PF doesn't apply as modern TV's have PFC.