    Dismiss Notice
calculating turns ratio in a transformer
Discussion in 'Homework Help' started by struglnstudnt, Sep 6, 2010.
  1. struglnstudnt
    struglnstudnt New Member
    Sep 6, 2010
    1
    0
    A transformer has a ratings plate: 4KVA
    Vp=400V
    Vs=80V
    Rp=1.5Ω
    Rs=0.1Ω
    I am aware that Vp/Vs=Np/Ns for the (ideal) transformer but how do I go about calculating the turns ratio for the above (real) transformer. Do I do the same calculation or is it different?
    Help on this would be much appreciated as I am struggling finding information on the internet for this question.
  2. colin55
    colin55 Well-Known Member
    Feb 14, 2009
    3,534
    82
    Melbourne Australia
    The turns ratio is 400:80
    For every 400 turns on the primary, you will put 80 turns on the secondary. All the other data is for other calculations.
    Your transformer may need 1 turn per volt and this will require 400 turns and 80 turns on the secondary.
    It may need 5 turns per volt 2000 turns to 400 turns
    or it may need 10 turns per volt. 4,000 turns to 800 turns The answer is always the same ratio of primary to secondary turns.
    In all cases you will get 80v out of the transformer.
  3. MrAl
    MrAl Well-Known Member Most Helpful Member
    Sep 7, 2008
    11,032
    952
    NJ
    ONLINE
    Hello,
    The transformer has primary voltage Vp at the terminals of 400v, secondary voltage Vs of 80v with full load, and primary current with full load Ip and secondary current Is with full load.
    One way to handle the transformer with primary and secondary resistances is to simply subtract the voltage dropped by the primary current and primary resistance from the primary voltage and use that as the new primary voltage, then add the voltage dropped by the secondary resistance and secondary current to the secondary voltage and call that the new secondary voltage, then take the ratio of the new secondary voltage to the new primary voltage and that will be the turns ratio required.
    If we formulize this process it comes out to this:
    A=(Vs+Is*Rs)/(Vp-Ip*Rp)
    where
    A is the turns ratio primary to secondary, and because this is a step down transformer you can take 1/A to be the turns ratio here, and
    Vs is the secondary voltage, and
    Vp is the primary voltage, and
    Is is the secondary current, and
    Ip is the primary current, and
    Rp is the primary resistance, and
    Rs is the secondary resistance.
    Example:
    We have 400v input and we want 80v output with load, and the primary resistance is 1.5 ohms and secondary resistance is 0.1 ohm, and the full load VA is 4kVA.
    The primary current is Ip=4000/400.
    The secondary current is Is=4000/80.
    The primary resistance Rp=1.5 ohms.
    The secondary resistance Rs=0.1 ohms.
    The primary voltage Vp is 400 volts.
    The secondary voltage Vs is 80 volts.
    Plugging these into the formula:
    we come out with:
    A=(80+50*0.1)/(400-10*1.5)
    and after doing the math we get:
    A=0.22077922
    which is the primary to secondary turns ratio, and the secondary to primary turns ratio is simply 1/A which is:
    1/A=4.52941176
    There is one more little catch here however, and that is that there is always some primary excitation current. To get more accurate results, we'd have to look up the excitation current from the manufacturers data sheet and figure that in as an additional voltage drop on the primary side.
    Colin:
    The turns ratio actually is usually made a little higher to make up for the loss of the primary and secondary resistances. The formula above takes these two resistances into account.
  4. dave
    Dave New Member
    Jan 12, 1997
    0
  5. unix60959
    unix60959 New Member
    Aug 31, 2010
    21
    2
    99.9% of the time ideal calculation are close enough for the device to work they way you want it to under 'real' conditions. if you want to know what the turns ratio has to be to make Vp=400V and Vs=80v then you best bet is to measure the input and output voltages and adjust the coils. Note that the resistive properties of the coils change with temperature also you voltage source of Vp is not going to be ideal either.
  6. jignesh doshi
    jignesh doshi New Member
    Mar 27, 2014
    1
    0
    hi MrAl,
    when i used this formulla for higher rating transformer then it's working fine but when i used for some small transformer then this formulla goes wrong, so please tell me is it right???
  7. MrAl
    Sep 7, 2008
    11,032
    952
    NJ
    ONLINE
    What formula are you using and what kind of transformer is the "higher rating" transformer, and what kind is the "small" transformer?
  8. audioguru
    audioguru Well-Known Member Most Helpful Member
    Mar 16, 2004
    32,447
    937
    Canada, of course!
    I have a cheap Chinese wall-wart. It is rated at 9VDC/200mA and it is accurate. But it produces 17.5VDC with no load so the turns ratio is made so that the resistance of its windings (it gets hot) is compensated for when it is loaded.