blueroomelectronics said:Is it a question? A statement?
Hayrettin Demir said:(Sorry , My English is very very bad).
RODALCO said:Need to know if HV ( 11kV or more )or LV cables. ( 230 / 400 V ).
...
...
I
RODALCO said:For HV cable megger readings should be high Mega ohms e.g. 300 M.ohms +.
Screens should give clear readings. e.g 33 kV cable screen should be able to hold 5 kV DC from megger. 100 M.ohms or more.
For locate: use dart for pre location of approx distance, then thumper for fault locate.
RODALCO said:I need to know what voltage your HT cable is ? 10 kV 11 kV 33 kV ?
A mimimum of a 5 kV megger is required. a 500 Volts megger hasn't got enough voltage to perhaps jump a gap in the insulation where a void is or a tree has formed in the cable insulation.
An AVO BM 25 is a great Megger for HV cables.
If you have access to VLF set it will let you know if an intermittand fault is present.
A VLF ( Very Low Frequency ) test is good practise to do on a suspect cable or after a repair.
For an 11 kV cable ( 6.3 kV to screen ) the test voltage is peaked to 17 kV at 0.1 Hz test frequency, for a period of 15 minutes, no breakdown shall occur.
Hero999 said:I'm a bit confused, I thought the test voltage needs to be higher than the working voltage. At work we use 500V for phase to eath and neutral for 230V systems and 1kV phase to phase for 400V systems. I haven't done any HV work but if I was asked to megger a 11kV installation I would use 20kV phase to phase and 10kV phase to earth.