Hello
I am designing a LPG transmitter to transmit a 4-20mA proportional output to sensed parameter.
I found the MQ6 to be a good candidate for this purpose.It measures a 300ppm to 10,000ppm of LPG change and converts to a 1.7V (normal condition) to 5V(max) of input ppm sensed.
For conversion to 4-20mA i am using a XTR111 from TI.
I saw few commercial transmitters and they have a procedure for calibrating the sensor out by setting zero and span.
Here is a section on one of the calibration procedures
Can some learned member guide me on educating me how this can be applied to my proposed design?
Please help even if its thinking out loud..
Thanks and regards
1 Check the input voltage to the transmitter, which should be 24V DC.
2 Check the head voltage of detector. Set it to 2V DC.
3 Insert the probes of the multi meter in to the Test pits (T.P). Check the milli volt reading. Set it
to 40mV (if required) with a tolerance of + / -3 mV using ‘ZERO’ trimpot.
4 Expose the detector with a known concentration of gas (flammable) through an adaptor
and tube at constant flow (i.e. 0.5 / 1 litre per minute) and allow the reading to get stabilized.
5 With respect to the concentration of the gas adjust the reading (if required), using SPAN or
‘S’trimpot with the probes still in the Test pits.
6 Stop the gas flow, remove the adaptor and allow the detector to settle down to zero i.e 40 mV
with a tolerance of + / -3mV.
7 If it does not settle down to zero, set it to ZERO approx 40mV + / -3 mV using ‘Z’ trimpot.
8 Repeat the above procedure (step 4 to 7) till proper calibration is achieved.
Thanks and regards