Definitions
Electrical Metallic Tubing (EMT)- A unthreaded thin walled raceway designed for protection and routing of conductors and cables. For use as an equipment grounding conductor when installed appropriate fittings. EMT is generally made of steel with protective coating or aluminum

Listed Requirements
EMT, factory elbows, fittings shall be listed by the underwriters Labratory
Installation

EMT is permitted for both exposed and concealed work

All supports, bolts, straps ,screws shall be corrosive resistant materials

Uses not permitted

Where Subject to sever physical damage.

Protected from corrosion solely by enamel

In cinder concrete or cinder fill where subject to permanent moister unless protection on all sides by a layer of non-cinder concrete at least 50mm thick or unless the tube is at least 450 under the fill

In any hazardous location except as permitted by the NEC

For support of luminaries or other equipment except conduit bodies no larger than the trade size of the tubing

Dissimilar metals in contact with anywhere in the system shall be avoided to avoid galvanic action

Size

Minimum- EMT smaller than trade size ½ inch cannot be used

Maximum-EMT bigger than trade size 4 shall not be used

Bends- How Made
Bends shall be made so the tubing is not damage and the internal diameter is not effectively reduced.

Number of Bends

There shall not be more than 4 quarter bends (360 degrees) between pull points

Reaming and threading

All cut ends of EMT shall be reamed or removed of rough edges

EMT shall not be threaded

Securing and supporting

EMT shall be fastened at least every 10ft

EMT shall be fastened within 3 ft of each outlet box, junction box, device box, cabinet, conduit body, or any other tubing termination

Couplings and connectors

Couplings and connectors shall be made up tight. Where buried in masonry or concrete, they shall be concrete tight

Grounding

EMT shall be permitted as an equipment grounding conductor

Construction

Factory threaded integral couplings shall be permitted. The coupling and EMT threads shall be designed so as to prevent bending of the tubing at any part of the tread
Marking

EMT shall be clearly and durably marked at least every 10 ft as required in the first sentence of 110.21
 

Attachments

  • EMT.pdf
    151.7 KB · Views: 595
  • EMT-tubing_chart.jpg
    EMT-tubing_chart.jpg
    80.1 KB · Views: 6,604