my 16 awg wire is rated at 10amps
my point is is it ok to put small wire before the breaker or i must absolutely put a big wire that can handle all the current of the primary breaker?
Reread the original post. He can not use the right pic because the wires will not go into the breaker.I would also say the right pic is better.its best too use a thicker wire than needed..using a smaller wire would cause heat that could be dangerous.
is it ok to put small wire before the breaker or i must absolutely put a big wire that can handle all the current of the primary breaker?
He can not use the right pic because the wires will not go into the breaker.
Or if you can get 3 10 AWG wires into the 30A breaker it would be the same thing, which I suggested several posts ago. Yes/no ?The left diagram is against the NEC, because the 16awg wires are being tripped by a 30A device. The right diagram is also against the NEC, because a breaker cannot have more than one wire on its terminal.
The correct answer would be to bring a 10 awg wire down from the breaker, to a terminal strip, and then 30A wires to each of the next set of breakers.
Or if you can get 3 10 AWG wires into the 30A breaker it would be the same thing, which I suggested several posts ago. Yes/no ?
Or if you can get 3 10 AWG wires into the 30A breaker
Hi just wondering if the method of wiring in the left of schematic is ok for UL approval, i know it would be best to do the right schematic but i can't enter physically 2 10awg in same breaker!
my 16 awg wire is rated at 10amps
i think that's what i'll do with standard terminals block, i was looking for a bus bar to fit my breakers but it is 2-3 weeks delivery, no store keeps them!Hi,
I would bring a 10awg wire from the 30 amp. breaker to a splitter box and, from there, another 10awg wire to each of the 10 amp. breakers. I would then be satisfied that it is safe. That is of course if it is possible to do it that way.
Alain