What country are you in?
What's the VA rating of your USA appliances and what is the maximum current a typical UK outlet can deliver?
Would you have all of the USA devices operating at the same time?
Most good barbers / stylists are converting over to LiPo battery and rotors motors - so much smoother to operate and less neuropathy. No frequency issues.With Americans coming to Europe, one type of appliance that is very frequency-sensitive is hair clippers. There are some threads about that on this forum.
https://www.electro-tech-online.com...s-240v-50hz-to-120v-60hz.130055/#post-1079191
With Americans coming to Europe, one type of appliance that is very frequency-sensitive is hair clippers. There are some threads about that on this forum.
https://www.electro-tech-online.com...s-240v-50hz-to-120v-60hz.130055/#post-1079191
Sorry, I was using 240/120 which are easier to come by. You can use those sorts of transformers on 220 to get 110V out.
Transformers can be placed in series to add or subtract voltages. Transformers can be paralleled if they are identical and must be phased properly.
Thats dones by connecting in series first so they add and you can determine the proper phase.
Maybe these are the options. I don;t know.
Submit your plans to the AHJ and obtain permits.
Suggestion, if allowed.
It looks like you need 2 circuits, with possibly two duplex outlets per circuit.
There might be available >10 A circuits, but not for the walls..
You can use one transformer or two. e.g. one per 10A circuit. 10*220 W.
or you can use one larger transfomer, and connect to to a circuit > 10A.
Someone mounts the transformer and two suitably sized breakers using standard DIN rail construction to give you two protected circuits.
Then see f you can use standard US outlets, boxes and Romex cable to your distribution point. Wire is 12 or 14 AWG,. Romex is also known as NM-b. The cable is flat and is known as 12-2 w/ground (20A)or 14-2 w/ground (15A). There are two insuleted conductors (black-HOT and White (Neutral) and an uninsulated one for ground.
That would likely be ideal.
if wiring is anything like this: https://www.alamy.com/stock-photo-electricity-wires-in-lahore-pakistan-37193699.html? which was taken in Pakistan, you shouldn't have a problem.
That's a good idea. I wonder if the UK will get sockets with that or something equivalent one day.Another characteristic of some newer outlets is called "tamper resistant". This really means "kid resistant" You cannot stick something in one of the holes and get shocked. You have to push both sides.