I have an hvac control panel that has a Honeywell logic panel w973f1004 with four heating relay outputs and two cooling relay outputs. These relay outputs cycle power to 208vac relays that energize contactor coils and solenoids. All relay outputs on the logic panel share the same common wire which is phase a of 208 vac. If I unhook all n.o. Relay wire connections and there are no wires connected to n.c. I have voltage on both n.c. And n.o. Of the relay output. I remove the logic panel and ohm all relay outputs using fluke 87 true rms and read 1 ohm from c to n.c. And OL from c to n.o. If I apply 115 volts to c and measure to neutral I read 115. From n.c. To neutral I read 115 if I check from n.o. To neutral I get 115 but the contact ohms as open. Somehow on this logic panel I am getting voltage from the common terminal to normally open. I have tried it on two new panels and one old panel and all have the same results. The problem it is causing is it is applying voltage to control relays causing them to chatter- only 85 to 130 vac to coil (a1 -a2) when it should be de-energized. This is causing relays to intermittently not open contacts as it is enough voltage to keep them pulled in after being energized. Is there any way to resolve this? How can the voltage be getting from common to normally open when the contacts ohm as open?? Thanks in advance for any advice.