Hi,
Recently tried but failed, I think, to get my point across about how to correctly use a relay.
The commercial temperature controller device, relay driven, is rated at 3kw @ 230vAC.
The users were connecting a 3kw heater to it and finding the relay would not last much more than a year ( perhaps being switched about 100 times a day)
I said how I typically derate power relays and such like by 30 to 50% to ensure good life and that for a 3kw load they would be better using a 20 or 30 Amp relay.
I used the comparison of driving the car at max revs all the time to highlight the point, but it fell on deaf ears.
Anyone suggest any evidence I can present to them to clearly emphasize the point in a non technical way ?
thanks.
Recently tried but failed, I think, to get my point across about how to correctly use a relay.
The commercial temperature controller device, relay driven, is rated at 3kw @ 230vAC.
The users were connecting a 3kw heater to it and finding the relay would not last much more than a year ( perhaps being switched about 100 times a day)
I said how I typically derate power relays and such like by 30 to 50% to ensure good life and that for a 3kw load they would be better using a 20 or 30 Amp relay.
I used the comparison of driving the car at max revs all the time to highlight the point, but it fell on deaf ears.
Anyone suggest any evidence I can present to them to clearly emphasize the point in a non technical way ?
thanks.