1. who uses DIY power supplies on a industrial automation project in this day and age?
2. if you do, make sure you get it right, 37V is not same as 24V, making basic power supply is easy (something you didn't manage so far). making really good one is not.
3. make sure you use appropriate suppressors on each and every inductive load. if you are using 24VDC to power up some solenoids, contactors or whatever (all of them are inductive loads), add diode in parallel to each.
4. Make sure suppressor (diode or MOV or whatever) is always installed in the right place - directly across the load (if you are installing suppressor but placing it away, you are doing big mistake).
5. Make sure suppressor is rated according to application.
6. what kind of power you need from this PSU? there are low cost versions, check Idec, Omron, etc.