I want to monitor the loading of an AC pump.....120VAC around 12amps.
Using a PIC. The intention is to decide if it is loaded or overloaded using the 12Amps as the trip.
I figure using a toroid (with the 120V line looped thru it) into a resistive load and then rectified by a schottky into a smoothing cap and then into biasing a 2n3904 on/off as an input drive to a digital input should do the trick.
Make sure you have a burden resistor on that toroid
f open-circuited with current flowing in the primary the transformer secondary will attempt to continue driving current into what is effectively an infinite impedance. This will produce a high and potentially dangerous voltage across the open secondary [1]
You'll get some variance using a transistor, an op amp comparator would give you good accuracy.
A proprietry current transformer would make things easier if you can get one.
You'll get some variance using a transistor, an op amp comparator would give you good accuracy.
A proprietry current transformer would make things easier if you can get one.