How many errors about electrical code ?

Status
Not open for further replies.

Externet

Well-Known Member
Hi.
A typical ordinary electric range/stove fed by split phase 230V and neutral (3 contacts) outlet on a 40A breaker feeds also a plain overhead fan/light hood assembly.

115V is taken from the outlet at the baseboard into the wall and up to the hood assembly on AWG16 'zip cord' cable.

Phase-----------------------------------------------------------------outlet--------------1A inline fuse-------------hood
Neutral---------------------------------------------------------------outlet--------------------------------------------hood
Phase-----------------------------------------------------------------outlet

There is no dedicated ground wire; just the neutral I assume bonds to the stove chassis?, and a metal conduit that ends at the outlet, appears to be original unmolested construction on a 1992 house.
How bad/dangerous/against electrical code is that ? Or was it perfectly normal then and code has been updated since ?

Picture borrowed from the net :
----> https://www.myrv.us/electric/img/N 10-50R 125-250-volt.jpg
 
The three prong outlet would be acceptable for pre 1996 construction.

The above quote taken from here. Note that continuing to use the three prong outlet is acceptable and if a new appliance is added just buy a three prong plug to mate with the outlet.

While we use gas for the stove when we renovated the laundry room I replaced the power to the clothes drier and installed a new 4 prong socket to mate with the new drier.

The zip cord in the wall is not acceptable. Minimum in the wall should be AWG 14. My father-in-law managed to start a small fire in a wall running zip cord to a home brew outlet.

Ron
 