    Hello,
    I wanted to measure water level up to 50 Mts with 5 cm accuracy. Can I use a pressure sensor for this purpose? I tried a pressure sensor with built in amplifier got from one supplier. I kept it at a depth of 2.5Mts of water and monitored the output throughout day time. I found a variation of 1.5% in the output voltage. What could be the reasons for such variations? Could it be due to the atmospheric pressure variation? Is there any way to compensate it?
    Your help will be highly appreciated.
     
  2. MCU88

    MCU88 Member

    Joined:
    Apr 1, 2015
    Messages:
    121
    Likes:
    7
    Is the water in an tank with known size? Have you considered using ultrasonic technology to measure water level where tiny echos are transmitted and received?
     
  3. premkumar9

    premkumar9 Member

    Joined:
    Oct 28, 2008
    Messages:
    513
    Likes:
    1
    Location:
    India
    Water in a dam. 50 Meters.
     
  4. dave

    Dave New Member

    Joined:
    Jan 12, 1997
    Messages:
    -
    Likes:
    0


     
  5. koolguy

    koolguy Active Member

    Joined:
    Aug 24, 2010
    Messages:
    2,196
    Likes:
    9

    Hello,
    There are many ultra sonic sensor are not good in this situation, i think because it sensor get wet due to evaporation.
    may be something like Electro magnet Reed switch?
     
  6. alec_t

    alec_t Well-Known Member Most Helpful Member

    Joined:
    Jul 10, 2011
    Messages:
    9,316
    Likes:
    1,230
    Location:
    Cardiff, Wales
    Have you checked the specs of available pressure sensors? You are asking for a resolution of 0.1%. I'd be surprised if any one sensor type would be linear to that accuracy, so multiple calibration points would probably be needed. This link describes various non-linearity components.
     
  7. JimB

    JimB Super Moderator Most Helpful Member

    Joined:
    Sep 11, 2004
    Messages:
    6,390
    Likes:
    592
    Location:
    Peterhead, Scotland
    Yes it is usually an expensive pressure transmitter that will give you 0.1% accuracy.

    Can you tell us which pressure transmitter you are using?

    Whether the Ptx will respond to atmospheric pressure depends on the type and configuration. More information required.

    JimB
     
  8. Reloadron

    Reloadron Well-Known Member Most Helpful Member

    Joined:
    Dec 23, 2009
    Messages:
    6,801
    Likes:
    282
    Location:
    Cleveland, Ohio USA
    While you do not mention the manufacturer or model number of the pressure sensor you used there are many variables that can effect your measurement over time. Temperature? Changes in atmospheric pressure? The uncertainty of the instrument used to measure the pressure sensor output? The excitation voltage applied to the sensor? Then you have the data sheet specifications of the sensor itself.

    You can have the 0.1% accuracy you desire but it requires, as was mentioned, more expensive pressure transmitters. Here is an example of an Omega Manufacture Smart Pressure Transmitter, High Stability, Low Drift pressure transducer. Just the transducer will cost about $2,300 USD and if we add a quality process meter we easily will exceed $3,000 USD. That is just an example, there are other manufacturers like Rosemount who make similar units in precision and cost.

    So what this comes down to is I can buy a pressure transducer/transmitter for about $25 USD or I can buy a pressure transducer/transmitter for about $2,500 USD depending on my needs. They will both measure pressure but one does a much, much better job but cost much, much more. :)

    What you are seeing is not at all unusual. I would start with a differential type sensor and work from there based on your uncertainty needs.


    Ron
     
  9. jpanhalt

    jpanhalt Well-Known Member Most Helpful Member

    Joined:
    Jun 21, 2006
    Messages:
    6,060
    Likes:
    519
    Location:
    Cleveland, OH, USA
    ONLINE
    There should be some reference point on the top or face of the dam that doesn't move. Can't you measure referenced to that?

    John
     
  10. cowboybob

    cowboybob Well-Known Member Most Helpful Member

    Joined:
    Oct 22, 2011
    Messages:
    3,050
    Likes:
    479
    Location:
    James Island, SC
    Your stated accuracy requirements are severe.

    Given the depth of the water, you need a pressure sensor in the ≈70 PSI range (0.445lb per column-foot).

    This site: http://www.astsensors.com/submersible_level_sensors/AST4500__AST4510

    has sensors that, I believe, meet your needs (accuracy, barometric pressure compensation, etc), but are very expensive, especially with their associated electronics.

    If I may ask, why the need for such accuracy (a 5cm depth differential would be overcome with a stiff wind "piling" up surface water)? jpanhalt's suggestion sounded inexpensive and easily implemented, if you're willing to accept a reduced accuracy.
     
  11. premkumar9

    premkumar9 Member

    Joined:
    Oct 28, 2008
    Messages:
    513
    Likes:
    1
    Location:
    India
    Thank you all for your replies. Normally Alerts come to my inbox when somebody replies. This time alerts came only for first 2 replies. So I didn't check the other replies. Now only the replies came to my notice. I will go through them in detail and revert. Once again thank you all.
     
  12. ericgibbs

    ericgibbs Well-Known Member Most Helpful Member

    Joined:
    Jan 4, 2007
    Messages:
    21,235
    Likes:
    645
    Location:
    Ex Yorks' Hants UK
    Hi,
    Many depth pressure sensors have a built in air vent pipe within the cable to the transducer.
    This ensures that the differential between the water pressure side of the sensor diaphragm and the atmospheric side compensates for changes in barometric pressure.
    The 2.5Bar depth transducer [~25mtrs] I used cost around ~£120, you can get 5Bar sensors [~50mtrs], which is the depth that you have specified.

    The 2.5Bar transducer gave water depth accuracy of +/-5cms.

    What maximum range of water depth 'change' do you expect to see in the dam water.???

    E
     
  13. premkumar9

    premkumar9 Member

    Joined:
    Oct 28, 2008
    Messages:
    513
    Likes:
    1
    Location:
    India
    30 meters
     
  14. ericgibbs

    ericgibbs Well-Known Member Most Helpful Member

    Joined:
    Jan 4, 2007
    Messages:
    21,235
    Likes:
    645
    Location:
    Ex Yorks' Hants UK
  15. Externet

    Externet Member

    Joined:
    Nov 14, 2006
    Messages:
    820
    Likes:
    24
    Location:
    Mideast U.S.
    For the original question; yes, a pressure transducer can be used. But I think that attaching a measuring tape to a dam wall would be much simpler, reliable, accurate, precise and long lasting.
     
  16. premkumar9

    premkumar9 Member

    Joined:
    Oct 28, 2008
    Messages:
    513
    Likes:
    1
    Location:
    India
    The data is to be sent to the server. So electronic measurement is required.
     
  17. premkumar9

    premkumar9 Member

    Joined:
    Oct 28, 2008
    Messages:
    513
    Likes:
    1
    Location:
    India
    I can fix an another pressure sensor at fixed location near the dam and take the readings. Can I use this readings to compensate the pressure variation due to atmospheric pressure change? Is this atmospheric pressure change the main reason for the drift in sensor output?
     
  18. ericgibbs

    ericgibbs Well-Known Member Most Helpful Member

    Joined:
    Jan 4, 2007
    Messages:
    21,235
    Likes:
    645
    Location:
    Ex Yorks' Hants UK
    You could use an external atmospheric pressure sensor to correct for changes in the readings, but the 'drift' may be due to other causes in the equipment being used

    It should be easy enough to test using the atmospheric pressure sensor,, record both the readings from the submerged sensor and the atmospheric sensor over a few hours,
    observing the actual water 'height' using a semi immersed calibrated water level board.

    Do you follow that OK.?
    E
     
  19. KeepItSimpleStupid

    KeepItSimpleStupid Well-Known Member Most Helpful Member

    Joined:
    Oct 30, 2010
    Messages:
    9,965
    Likes:
    1,099
    The datasheet Eric linked to had, pressure, density @ temperature and G.

    I THINK if one were to look at relative height, you would need a ported sensor or one related to differential pressure. So, i would think you would need calm waters.
    Acceleration due to gravity varies. See: http://www.blazelabs.com/f-u-massvariation.asp. Density will vary with temperature. If then sensor has any smart, the temperature would be measured at the sensor. The temperature may not be the same over the measured distance.

    Further remember that the pressure REPORTED by the weather bureau is NORMALIZED to sea level even if your 5000 ft up.

    You have a lot of potential error sources because this isn't a tank on the ground.

    Now, I'm wondering if you could do a differential sort of measurement to a known depth (floating sensor).

    Say the floating sensor is 1 foot under water, but it reports a value of 13". Your sensor reports 26' The density of the water may change with temperature and depth.
    So, you sort of normalize it.

    These are just ideas.I haven't worked in the field. I have had hydraulics and relativity in class, but don't remember much.
     
  20. ericgibbs

    ericgibbs Well-Known Member Most Helpful Member

    Joined:
    Jan 4, 2007
    Messages:
    21,235
    Likes:
    645
    Location:
    Ex Yorks' Hants UK
    hi,
    You may get a better understanding by reading this PDF.
    E
     

    Attached Files:

    • Like Like x 1
    • Informative Informative x 1
  21. premkumar9

    premkumar9 Member

    Joined:
    Oct 28, 2008
    Messages:
    513
    Likes:
    1
    Location:
    India
    I understand like this. The actual pressure sensor output from the sensor immersed in water at a known depth and the output voltage from a sensor at fixed position has to be compared over a period of time to understand their relationship. From this a correction factor can be worked out. Am I right?
     